Physics · Article
Engines, refrigerators, and heat pumps
Follow heat and work through complete cycles, distinguish efficiency from cooling/heating COP, apply conditional reversible limits, and connect vapor-compression components, ideal cycles and finite-rate models to honest performance boundaries.
Previous article: Entropy and the second law
Back to PhysicsAfter reading, you can
- Close cyclic heat/work balances with explicit directions, signs, units and useful output.
- Distinguish thermal efficiency, cooling/heating COP, capacity and system/seasonal boundaries.
- Apply reversible two-reservoir limits using kelvin temperatures and explain their conditions.
- Explain vapor-compression components and use a bounded steady enthalpy ledger.
- Compare explicit Carnot/Otto and finite-conductance models while retaining their regimes and limits.
Why does a refrigerator warm the room?
Suppose a refrigerator removes 1200 J from its cold compartment in one cycle while receiving 400 J of work into its stated cycle. How much energy must its warm-side coils release into the room? Could opening the door cool the whole room? These questions begin with the energy crossing a chosen boundary, before any efficiency formula.
If the working fluid returns to its initial state each cycle, its stored energy has no net change. The warm side must therefore release 1600 J: the 1200 J removed from the compartment plus the 400 J input. The refrigerator moves energy from a colder region to a warmer one while adding its work input to the warm-side delivery.
Use assigned reservoir temperatures of 270 K and 300 K for this teaching case. A reservoir is an ideal source or sink that exchanges energy while retaining its temperature. A finite room or a cooling object is not exactly such a reservoir; its temperature can change. None of the assigned cases below is a measured device rating.
For a first reading, follow the energy directions, engine efficiency, the two coefficients of performance, reversible bounds, temperature lift and the four-component refrigerator. Sections marked “Further” offer a return path through explicit gas cycles, finite-conductance power and an entropy audit. Published preparation is “Physical systems, states, boundaries, and environments” and “Units, standards, and physical constants”. The needed energy, cycle and temperature terms are defined here; neighboring thermodynamics lessons are follow-on support, not assumed live prerequisites.
A cycle restores the working substance, not the surroundings
A working substance is the material whose state changes while an engine or refrigerator operates. A thermodynamic cycle returns that material to its initial state. Its internal energy U, a state quantity, therefore has ΔU = 0 over the full cycle, even though heat and work have crossed its boundary. Reservoirs and a load can have changed after it completes the cycle.
Use signed heat Q positive into the working substance and signed work W_by positive out. The closed-system first law is ΔU = Q − W_by, neglecting endpoint kinetic and gravitational changes. Over a cycle, net heat into that system equals net work out. A continuously flowing plant instead needs a control-volume balance, including the energy carried by entering and leaving mass.
To keep heat arrows readable, Q_H and Q_C below are nonnegative magnitudes of hot-side and cold-side exchanges, with their directions stated separately. They are not both signed heat inputs. An engine receives Q_H from the hot source and rejects Q_C to the cold sink. A refrigerator receives Q_C from the cold region and rejects Q_H to the warm region while receiving work W_in.
Energy per cycle is in joules. A rate, written with a dot or described as power, is in watts: 1 W = 1 J/s. Multiplying a per-cycle quantity by cycles per second gives its average rate only for the stated repeatable operation. Startup, stored-energy changes, defrost and changing loads may require a longer time-dependent balance.
| Purpose | Hot-side exchange | Cold-side exchange | Work and balance |
|---|---|---|---|
| Engine | Q_H enters device | Q_C leaves device | W_out = Q_H − Q_C leaves |
| Refrigerator | Q_H leaves device | Q_C enters device | W_in = Q_H − Q_C enters |
| Heat pump in heating mode | Q_H leaves toward useful warm load | Q_C enters from colder source | W_in = Q_H − Q_C enters |
An engine converts part of heat input into net work
Thermal efficiency is η = W_out/Q_H = 1 − Q_C/Q_H for a cyclic engine with the stated two heat exchanges and no other energy input. It compares useful net work to heat supplied, rather than gross expansion work before compression or pump costs are subtracted.
For a separate assigned engine, take Q_H = 2000 J and Q_C = 1200 J per cycle. Then W_out = 800 J and η = 0.400, or 40.0%. At 5.00 cycles/s, the heat-input rate is 10.0 kW, rejection is 6.00 kW and net output is 4.00 kW. The rates close the same balance as the per-cycle values.
A cold sink is part of the thermal-engine arrangement. A cyclic device cannot have as its only effect the extraction of heat from a single reservoir and its complete conversion into work. That second-law restriction is stronger than energy conservation. A battery or fuel cell has other forms of energy change; applying a two-reservoir heat-engine formula blindly to its entire input misidentifies the conversion.
Practical plant efficiency also depends on the declared boundary: shaft work, generator output and net exported electrical energy differ when generators, pumps, fans and other loads are included. A cogeneration plant supplies useful heat as well as work; adding both useful outputs can describe energy utilization, but does not turn all delivered heat into work or make its thermal efficiency the same number.
One reversed cycle, two useful outputs
A refrigerator is judged by the heat removed from the cold region. Its coefficient of performance is COP_R = Q_C/W_in. A heating heat pump is judged by heat delivered to the warm region: COP_HP = Q_H/W_in. For the same cycle, boundary and operating condition, Q_H = Q_C + W_in gives COP_HP = COP_R + 1.
The opening assigned cycle has COP_R = 1200/400 = 3.00 and COP_HP = 1600/400 = 4.00. A COP above one does not mean that more energy was created than supplied. The useful heating output includes energy taken from the colder source as well as the work input. COP is not a heat-to-work thermal efficiency.
At the assigned 2.00 cycles/s, this cycle removes 2.40 kW, receives 0.800 kW of work and rejects 3.20 kW. Cooling capacity means a rate of heat removal; it is not the same quantity as COP. Two devices can have equal COP but very different capacity, or equal capacity but different input power.
An open refrigerator door inside one otherwise closed room does not provide an external cold source. Heat it removes from room air is returned to that same room along with the electrical input, so its net effect adds that input to room energy under the stated boundary. In normal operation the insulated cold compartment is a distinct useful region; an air conditioner rejects heat outside the space it cools.
Follow the energy, then choose the useful output
Two separate reservoir-and-device diagrams compare the assigned engine and refrigerator. Cooling and heating evaluate different useful outputs of the same displayed refrigerator cycle, without changing its energy arrows.
Stack the two diagrams on narrow readers and keep their temperature labels beside the correct reservoirs.
Engine: 600 K hot reservoir and 300 K cold reservoir.
Refrigerator: 270 K cold region and 300 K warm reservoir.
- Solid thermal arrows with filled arrowheads: heat exchange.
- Dashed work arrows with open arrowheads: work exchange.
2000 J per cycle enters from the hot source.
1200 J per cycle leaves for the cold sink.
800 J per cycle leaves as net work.
Thermal efficiency: 800/2000 = 0.400.
1200 J per cycle enters from the cold region.
400 J per cycle enters as work.
1600 J per cycle leaves toward the warm region.
Cooling purpose counts the 1200 J removed: COP_R = 3.00.
Heating purpose counts the same cycle’s 1600 J delivered: COP_HP = 4.00.
For this same cycle and boundary, COP_HP = COP_R + 1.
The working substance returns to its initial state: ΔU_cycle = 0.
All displayed transfer amounts are nonnegative magnitudes; arrow direction supplies the sign.
Arrow widths are schematic, not proportional energy widths.
J per cycle is energy; multiplying by cycles/s gives average W.
With an open door inside one otherwise closed room, the refrigerator adds its work input to room energy.
These assigned operating points lie below their own reversible limits; the two panels have different reservoir temperatures.
Compare balances and useful-output ratios using each panel’s own boundary.
| Case | Q_H (J) | Q_C (J) | Work magnitude (J) | Useful-output ratio |
|---|---|---|---|---|
| Engine | 2000 | 1200 | 800 | η = 0.400 |
| Same refrigerator, cooling purpose | 1600 | 1200 | 400 | COP_R = 3.00 |
| Same refrigerator, heating purpose | 1600 | 1200 | 400 | COP_HP = 4.00 |
What two reservoir temperatures can tell us
A reversible process is an ideal limiting process that can be reversed while restoring both system and surroundings without a residual change. Quasistatic motion alone does not remove friction, a finite-temperature heat-transfer difference or throttling irreversibility. A reversible cycle between two fixed-temperature reservoirs provides a performance bound, not a blueprint for a real machine at a promised output rate.
For T_H > T_C > 0 on the absolute kelvin scale, the maximum engine efficiency is η_rev = 1 − T_C/T_H. Reversing the reversible exchange ratio Q_C/Q_H = T_C/T_H gives COP_R,rev = T_C/(T_H − T_C) and COP_HP,rev = T_H/(T_H − T_C). Actual devices with the same two-reservoir boundary cannot exceed these values.
For the assigned engine at 600 K and 300 K, η cannot exceed 0.500. Its assigned 0.400 lies below that bound. A proposed 2000 J input, 800 J rejection and 1200 J work would conserve energy but have efficiency 0.600, above the bound; that two-reservoir cyclic claim is rejected.
For the opening refrigerator at 270 K and 300 K, the reversible cooling and heating COPs are 9.00 and 10.0. Its assigned values 3.00 and 4.00 are below those bounds. Removing the same 1200 J would require at least 133.333 J of work in the reversible limit. Temperature ratios using 0 °C and 30 °C would be invalid; offsets do not cancel in ratios.
| Case | Assigned performance | Reversible bound | Meaning |
|---|---|---|---|
| Engine: 600/300 K | η = 0.400 | η ≤ 0.500 | 800 J net work from 2000 J input |
| Refrigerator: 300/270 K | COP_R = 3.00 | COP_R ≤ 9.00 | 1200 J removed for 400 J input |
| Same cycle, heating purpose | COP_HP = 4.00 | COP_HP ≤ 10.0 | 1600 J delivered for 400 J input |
Why changing the working fluid cannot beat that bound
Imagine a proposed engine more efficient than a reversible engine between the same reservoirs. Run the reversible device backward, and scale it so that the two work transfers cancel. The combined arrangement would move heat from the cold reservoir to the hot one with no other net effect. The second law excludes that result. Interchanging the two reversible devices similarly shows why they must share the same limiting efficiency.
The argument concerns complete cycles and all their external effects. Cooling a finite hot body once, consuming fuel, draining a battery or changing another reservoir is an additional effect. Such cases are not counterexamples to the two-reservoir cyclic bound; they require the corresponding larger energy and state balance.
A different working fluid can greatly affect attainable temperatures, pressures, heat-transfer rates, safety, losses and practical performance. It does not change the reversible bound for the same external reservoir temperatures. Conversely, a gas cycle that exchanges heat over a range of temperatures does not automatically attain the Carnot efficiency evaluated from its hottest and coldest working-fluid states.
Temperature lift and a declared heating load
Temperature lift is the hot-to-cold temperature difference in the stated model. Raising T_H or lowering T_C increases that lift and lowers the reversible heat-pump COP. For a fixed useful heating rate, the corresponding reversible minimum work rate is W_min = Q_H(T_H − T_C)/T_H. Larger lift requires more minimum input for that same load.
Hold the useful hot side at 308.15 K and compare five colder-source temperatures. The table varies only the reversible bound, not an assumed actual COP curve. Reservoir temperatures are external references; a real refrigerant must usually be warmer than the heated medium in its condenser and colder than the source in its evaporator to transfer heat at a finite rate.
At the separate assigned operating point T_C = 273.15 K, a building receives 6.00 kW from a compressor cycle with heating COP 3.20. Compressor input is 1.875 kW and extracted source heat is 4.125 kW. Include an additional 0.200 kW auxiliary load stipulated to dissipate outside the heated envelope: wall input is 2.075 kW and whole-system useful heating COP is about 2.892.
Over one hour at those constant assigned conditions, wall energy is 2.075 kWh. The stipulated lossless resistance-heating comparator would use 6.00 kWh for the same useful heat. These are model calculations, not a seasonal rating or purchasing comparison. If auxiliary dissipation instead enters the heated space, or defrost changes delivered heat, the useful-output balance must change too.
Temperature lift changes a bound, not an equipment rating
Two aligned cold-reservoir-temperature panels show reversible heating/cooling COP bounds and minimum input for a fixed heating load. Isolated assigned operating points display compressor and whole-system boundaries without inventing actual performance curves.
Stack panels on narrow readers; preserve shared temperature range and visible power/COP units.
- Blue solid curve and circles: reversible heating COP.
- Orange dashed curve and squares: reversible cooling COP.
- Green dash-dot curve and triangles: reversible minimum input for heating.
- Filled diamond: assigned compressor point. Hollow square: whole-system point including stated outside auxiliaries.
Fixed hot reservoir T_H = 308.15 K.
At T_C = 273.15 K: assigned compressor COP_HP = 3.20, input 1875 W.
Same operating point, outside auxiliaries included: useful COP ≈ 2.891566, wall input 2075 W.
These isolated assigned points are not actual COP curves or measured ratings.
At the assigned point: 4125 W is extracted from the source.
Auxiliary input is 200 W stipulated to dissipate outside the heated envelope.
Reversible curves use only two fixed-temperature reservoirs and zero total entropy generation.
A large ratio at small lift does not guarantee finite heat-transfer rate or unlimited capacity.
Reservoir temperatures are not automatically the refrigerant evaporating and condensing temperatures.
Linear COP panel: T_C = 253.15–293.15 K, COP = 0–22.
Linear input panel: same T_C range, power = 0–2200 W.
Five exact reservoir temperatures and both assigned input boundaries have complete numeric equivalents.
| T_C (K) | Lift (K) | COP_HP,rev | COP_R,rev | Minimum input (W) |
|---|---|---|---|---|
| 253.15 | 55.00 | 5.602727 | 4.602727 | 1070.907026 |
| 263.15 | 45.00 | 6.847778 | 5.847778 | 876.196657 |
| 273.15 | 35.00 | 8.804286 | 7.804286 | 681.486289 |
| 283.15 | 25.00 | 12.326000 | 11.326000 | 486.775921 |
| 293.15 | 15.00 | 20.543333 | 19.543333 | 292.065552 |
| Input boundary | Useful heating (W) | Input (W) | Useful heating COP |
|---|---|---|---|
| Compressor cycle | 6000 | 1875 | 3.200000 |
| Wall input incl. outside auxiliaries | 6000 | 2075 | 2.891566 |
| T_C (K) | Lift (K) | COP_HP,rev | Minimum input (W) |
|---|---|---|---|
| 253.15 | 55.00 | 5.602727 | 1070.907026 |
| 263.15 | 45.00 | 6.847778 | 876.196657 |
| 273.15 | 35.00 | 8.804286 | 681.486289 |
| 283.15 | 25.00 | 12.326000 | 486.775921 |
| 293.15 | 15.00 | 20.543333 | 292.065552 |
How a vapor-compression loop moves heat
A common refrigerator or heat pump circulates a refrigerant through a compressor, condenser, expansion valve and evaporator. In the usual dry-compression arrangement, low-pressure vapor enters the compressor. Shaft work raises its pressure and generally its temperature enough that it can release energy to the warm side.
In the high-pressure condenser, the refrigerant rejects energy and commonly condenses to liquid; its temperature must support heat transfer toward the warmer useful load or room. The liquid then passes through a restriction to the low-pressure side. An approximately adiabatic valve with no shaft work and negligible kinetic and gravitational changes has nearly equal inlet and outlet enthalpy, not a useful work output.
At a suitable low pressure, part of the refrigerant can flash into vapor through the valve. The resulting cold stream absorbs energy in the evaporator and vaporizes before returning to the compressor. Pressure establishes the relevant phase-equilibrium temperature for a chosen fluid; compression does not simply “make cold”, and a valve is not an isentropic turbine.
The usual valve/evaporator cooling behavior depends on the refrigerant and its state. Isenthalpic does not mean universally cooling, and enthalpy values alone do not establish pressure, temperature or vapor quality. Superheating, subcooling, pressure drops and real compressor performance change the detailed cycle. A reversible thermodynamic cycle is not obtained simply by reversing the motor of this irreversible loop.
Use enthalpy for the flowing components
For steady flow, mass carries internal energy and the pressure–volume contribution needed to enter or leave a component. Their sum per mass is specific enthalpy h = u + pv, with u in J/kg, pressure p in Pa and specific volume v in m³/kg. Under the stated negligible kinetic/gravitational changes, the component energy balance relates heat and shaft work to enthalpy differences.
Use a separate synthetic ledger: h₁ = 400, h₂ = 450, h₃ = 250 and h₄ = 250 kJ/kg at suction, compressor outlet, condenser outlet and valve outlet. The compressor requires h₂−h₁ = 50 kJ/kg; the condenser releases h₂−h₃ = 200 kJ/kg; the evaporator absorbs h₁−h₄ = 150 kJ/kg. Their equality 200 = 150 + 50 is the same cycle balance as before.
At an assigned mass flow of 0.0200 kg/s, these become 1.00 kW input, 4.00 kW warm-side delivery and 3.00 kW cooling. The cooling and heating COPs are 3.00 and 4.00 for this ledger. Multiply kJ/kg by kg/s and by 1000 to obtain W; overlooking that conversion gives a thousandfold error.
These supplied h values are not a property table for a named fluid and do not validate a physical pressure/phase design. Actual analysis also checks refrigerant properties, pressure levels, dry compressor inlet, material and operating limits, energy leaks and component efficiencies. A p–v loop area for a closed piston gas is not automatically the shaft work of a continuously flowing compressor circuit.
Four components, one flowing energy ledger
An original directed refrigerant circuit connects compressor, condenser, throttle and evaporator. Separate heat/work arrows use the synthetic ledger. High/low pressure and usual phase roles are conditional mechanism labels, not properties inferred from the supplied enthalpies.
Use a contained circuit drawing or stacked component sequence; keep state numbers and energy arrows readable.
- Solid directed piping arrows identify circulating refrigerant mass flow.
- Separate labeled arrows identify heat or shaft-work transfer across each component.
1→2: compressor receives shaft work; usual dry vapor suction.
2→3: high-pressure condenser releases heat to the warm side.
3→4: restriction lowers pressure; no shaft work in this valve model.
4→1: low-pressure evaporator absorbs heat from the cold region.
High-pressure side: compressor outlet through condenser to valve inlet.
Low-pressure side: valve outlet through evaporator to compressor inlet.
State 1: h₁ = 400 kJ/kg.
State 2: h₂ = 450 kJ/kg.
State 3: h₃ = 250 kJ/kg.
State 4: h₄ = 250 kJ/kg.
Assigned steady mass flow: 0.0200 kg/s.
Compressor work input: 50.0 kJ/kg = 1000 W.
Condenser heat output: 200.0 kJ/kg = 4000 W.
Evaporator heat input: 150.0 kJ/kg = 3000 W.
4000 W delivered = 3000 W extracted + 1000 W input.
h₃ = h₄ follows from the stated steady adiabatic no-work throttle balance; it is not an isentropic turbine.
Synthetic enthalpies do not establish actual pressures, temperatures, phases or vapor quality.
Condensation, flash evaporation and dry suction describe the usual intended regime, requiring compatible refrigerant properties.
Isenthalpic expansion does not universally cool every substance and state.
For this ledger: COP_R = 3.00 and COP_HP = 4.00.
Component sizes and pipe lengths are schematic, not scale drawings or pressure magnitudes.
Port enthalpies and component energy rates reproduce the entire synthetic ledger.
| State | Location | h (kJ/kg) |
|---|---|---|
| 1 | Compressor inlet | 400.0 |
| 2 | Compressor outlet / condenser inlet | 450.0 |
| 3 | Condenser outlet / valve inlet | 250.0 |
| 4 | Valve outlet / evaporator inlet | 250.0 |
| Component | Transfer direction | Specific transfer (kJ/kg) | Rate (W) |
|---|---|---|---|
| Compressor | Work in | 50.0 | 1000 |
| Condenser | Heat out | 200.0 | 4000 |
| Valve | No shaft work | 0.0 | 0 |
| Evaporator | Heat in | 150.0 | 3000 |
| Component | Specific transfer (kJ/kg) | Rate (W) | Condition |
|---|---|---|---|
| Compressor: work in | 50.0 | 1000 | Adiabatic; h₂−h₁ |
| Condenser: heat out | 200.0 | 4000 | h₂−h₃ |
| Valve: no shaft work | 0.0 | 0 | h₃=h₄ in stated balance |
| Evaporator: heat in | 150.0 | 3000 | h₁−h₄ |
What a real performance figure includes
Real heat exchangers need driving temperature differences; friction and pressure drops dissipate work, and nonideal compression raises required input. Fans, pumps, controls, crankcase heating, cycling, startup and frosting or defrost can also matter at the declared system boundary. A single compressor-cycle COP does not by itself describe all energy purchased or all heat delivered over a season.
The heating or cooling capacity may change with source temperature and operating limits. A large COP at very small ideal temperature lift does not imply unlimited cooling power or finite heat transfer across zero temperature difference. The useful rate depends on heat-exchanger size, driving differences, flow and the specific machine.
A seasonal ratio is generally total useful energy delivered divided by total relevant input energy over its specified conditions. It is not the unweighted arithmetic mean of point COPs. Test procedures may use different units and include different loads, so convert units and inspect the declared conditions before comparing figures.
For air-source operation, frosting can obstruct the outdoor heat exchanger and defrost can temporarily change power and useful output. Ground- and water-source arrangements have different source conditions and auxiliary demands. These mechanisms explain why a theoretical bound and an assigned single operating point are useful checks but not substitutes for a full system measurement.
Different cycle families answer different physical questions
A Carnot cycle specifies reversible isothermal heat exchange connected by reversible adiabatic changes. It supplies the two-reservoir benchmark. An ideal Otto cycle instead represents compression, rapid heat addition near fixed volume, expansion and fixed-volume heat rejection of a closed gas surrogate. A real spark-ignition engine also exchanges mass and releases chemical energy, so that surrogate needs explicit limits.
The ideal Brayton gas-turbine model uses reversible adiabatic compression and expansion connected by approximately constant-pressure heat addition and rejection. Compressor input must be subtracted from turbine output. A real open gas turbine has intake and exhaust; its closed working-fluid cycle is a modeling construction, with the environment providing the return process.
A Rankine vapor-power model uses liquid pumping, high-pressure heating/vaporization, turbine expansion and low-pressure condensation. Pumping a dense liquid and expanding vapor differ from compressing a gas throughout. Phase properties, turbine wetness, pressure losses and heat-source temperatures shape its useful operating regime; it is not a Carnot steam engine simply because it uses boiling and condensation.
Refrigeration can also use an expansion device that recovers work or a reversed gas cycle when the application warrants it. Heat-driven absorption systems use an additional thermal input and a solution/regeneration mechanism; their thermal COP denominator differs from the electrical-work denominator used here. Include every generator, absorber, pump and heat exchange before applying a balance or comparing ratios. Detailed engineering and phase/potential models belong to their respective follow-on subjects.
Further: follow all four states of a Carnot gas cycle
For an explicit original realization, choose n = 1.00 mol of ideal gas with pV = nRT and R = 8.31446261815324 J/(mol K). Here C_p and C_V are total heat capacities at constant pressure and volume. Assign their constant ratio γ = C_p/C_V = 1.40; the ideal-gas relation C_p−C_V = nR gives C_V = nR/(γ−1), with ΔU = C_VΔT for this caloric model. Work is frictionless reversible pressure–volume work W_by = ∫p dV. This interpretation requires those conditions, rather than a curve drawn through arbitrary irreversible endpoints.
At 600 K, A→B expands isothermally from 0.0100 to 0.0200 m³ and absorbs Q_H = nRT_H ln 2 ≈ 3457.888 J. Reversible adiabatic B→C lowers the gas to 300 K; with constant γ, TV^(γ−1) is constant. It reaches V_C ≈ 0.113137 m³. Isothermal C→D at 300 K releases about 1728.944 J while compressing to V_D ≈ 0.056569 m³.
Adiabatic D→A completes the state cycle at 600 K and 0.0100 m³. The two adiabatic work transfers are equal and opposite for this assigned ideal gas because their temperature changes reverse. Net work is about 1728.944 J, and η = 0.500. The four branch changes individually obey ΔU = Q − W_by and sum to zero in U.
The clockwise p–V loop has net work equal to its signed enclosed area under these quasistatic pressure–volume conditions. Reversing all four reversible branches gives net input work and reversed heat exchanges. Isotherms need reversible thermal contact with their reservoirs, while the adiabats need thermal isolation. The detailed entropy lesson explains why reversibility is the decisive restriction.
Further: an Otto model and its conditional compression-ratio trend
For a separate one-mole constant-γ ideal-gas surrogate, start at T₁ = 300 K and V₁ = 0.0100 m³. Let compression ratio r = V₁/V₂ = 8.00 and peak T₃ = 1800 K, with γ = 1.40. The reversible adiabats give T₂ = T₁r^(γ−1) ≈ 689.219 K and T₄ = T₃/r^(γ−1) ≈ 783.496 K.
Fixed-volume heat addition is Q_H = C_V(T₃−T₂) ≈ 23088.867 J and rejection magnitude is Q_C = C_V(T₄−T₁) ≈ 10050.013 J. Net work is about 13038.854 J. Substituting both adiabatic relations gives η_Otto = 1−r^(1−γ) ≈ 0.564725.
This efficiency depends on r and the assigned constant γ within this model. It does not say that a real engine can increase compression ratio indefinitely: ignition/knock, material limits, changing heat capacities, combustion timing, heat loss, friction and gas exchange matter. Nor is it a comparison with the 600/300 K Carnot example; this surrogate has different temperatures and heat-exchange conditions.
During the Otto constant-volume heat exchanges, working-fluid temperature changes. A reversible realization would require matched changing-temperature heat sources/sinks rather than one hot and one cold isotherm. The paired cycle figures therefore retain separate pressure and volume scales and do not compare loop areas as if they belonged to the same device or energy input.
Different heat-exchange paths make different gas cycles
Two independently scaled p–V plots retain every original Carnot and Otto branch. State markers, direction arrows and complete signed transfer tables explain the cycle differences without equating unlike loop areas.
Stack the two gas plots at narrow widths and keep each plot’s own scales and legends attached.
Left panel: assigned one-mole Carnot gas cycle at 600/300 K.
- A→B, blue solid line and circles: reversible hot isothermal expansion.
- B→C, orange dashed line and squares: reversible adiabatic expansion.
- C→D, green dash-dot line and triangles: reversible cold isothermal compression.
- D→A, light dotted line and diamonds: reversible adiabatic compression.
Right panel: separate one-mole Otto surrogate, r = 8.00, γ = 1.40.
- 1→2, blue solid line and circles: reversible adiabatic compression.
- 2→3, orange dashed line and squares: constant-volume heat addition.
- 3→4, green dash-dot line and triangles: reversible adiabatic expansion.
- 4→1, light dotted line and diamonds: constant-volume heat rejection.
Direction arrows and distinct numbered/lettered state markers follow each complete clockwise cycle.
With the stated quasistatic p–V work only, signed loop area equals each gas cycle’s own net work.
A closed-gas p–V area is not automatically the shaft work of the flowing refrigerant circuit.
Carnot net work ≈ 1728.944 J; η = 0.500.
Otto net work ≈ 13038.854 J; η ≈ 0.564725 under its separate assumptions.
The panels have different temperatures, heat inputs and axis scales; loop areas are not a common-condition performance comparison.
Carnot axes: V = 0–0.120 m³; p = 0–550 kPa, both linear.
Otto axes: V = 0–0.0110 m³; p = 0–13000 kPa, both linear.
Stored pressure values are Pa; divide by 1000 for the visible kPa coordinate.
Fixed amount, ideal gas and assigned constant γ = 1.40 in each explicit realization.
Otto heat exchange occurs over changing gas temperatures; Carnot heat exchange is isothermal.
No real combustion, variable heat capacity, mass exchange, friction, pressure loss or engine rating is predicted.
State volumes, pressures and temperatures identify every branch endpoint.
Signed Q, W_by and ΔU close each branch and the complete cycle.
State A: T ≈ 600.000 K, V ≈ 0.010000 m³, p ≈ 498.868 kPa.
State B: T ≈ 600.000 K, V ≈ 0.020000 m³, p ≈ 249.434 kPa.
State C: T ≈ 300.000 K, V ≈ 0.113137 m³, p ≈ 22.047 kPa.
State D: T ≈ 300.000 K, V ≈ 0.056569 m³, p ≈ 44.094 kPa.
State 1: T ≈ 300.000 K, V ≈ 0.010000 m³, p ≈ 249.434 kPa.
State 2: T ≈ 689.219 K, V ≈ 0.001250 m³, p ≈ 4584.389 kPa.
State 3: T ≈ 1800.000 K, V ≈ 0.001250 m³, p ≈ 11972.826 kPa.
State 4: T ≈ 783.496 K, V ≈ 0.010000 m³, p ≈ 651.434 kPa.
| State | T (K) | V (m³) | p (kPa) |
|---|---|---|---|
| A | 600.000000 | 0.010000000 | 498.867757 |
| B | 600.000000 | 0.020000000 | 249.433879 |
| C | 300.000000 | 0.113137085 | 22.047048 |
| D | 300.000000 | 0.056568542 | 44.094097 |
| Branch | Kind | Q (J) | W_by (J) | ΔU (J) |
|---|---|---|---|---|
| A→B | isothermal | 3457.887793 | 3457.887793 | 0.000000 |
| B→C | adiabatic | 0.000000 | 6235.846964 | -6235.846964 |
| C→D | isothermal | -1728.943896 | -1728.943896 | 0.000000 |
| D→A | adiabatic | 0.000000 | -6235.846964 | 6235.846964 |
| State | T (K) | V (m³) | p (kPa) |
|---|---|---|---|
| 1 | 300.000000 | 0.010000000 | 249.433879 |
| 2 | 689.219013 | 0.001250000 | 4584.388575 |
| 3 | 1800.000000 | 0.001250000 | 11972.826170 |
| 4 | 783.495507 | 0.010000000 | 651.434410 |
| Branch | Kind | Q (J) | W_by (J) | ΔU (J) |
|---|---|---|---|---|
| 1→2 | adiabatic | 0.000000 | -8090.367335 | 8090.367335 |
| 2→3 | isochoric | 23088.867483 | 0.000000 | 23088.867483 |
| 3→4 | adiabatic | 0.000000 | 21129.221521 | -21129.221521 |
| 4→1 | isochoric | -10050.013297 | 0.000000 | -10050.013297 |
| Compression ratio r | T₂ (K) | T₄ (K) | Efficiency η |
|---|---|---|---|
| 4.00 | 522.330338 | 1033.828519 | 0.425651 |
| 6.00 | 614.301753 | 879.046815 | 0.511641 |
| 8.00 | 689.219013 | 783.495507 | 0.564725 |
| 10.00 | 753.565929 | 716.592907 | 0.601893 |
Further: finite heat transfer can separate maximum power from maximum efficiency
Consider a bounded original model: a reversible internal engine works between θ_H and θ_C, while external reservoirs are at 600 K and 300 K. Heat crosses two finite linear conductances K_H = K_C = 10.0 W/K. Thus Q̇_H = K_H(T_H−θ_H) and Q̇_C = K_C(θ_C−T_C). The internal reversible ratio is Q̇_C/Q̇_H = x = θ_C/θ_H; this does not make the external heat transfers reversible.
Solving the two balances gives θ_H = (K_HT_H + K_CT_C/x)/(K_H+K_C) and θ_C = xθ_H. With K_eff = K_HK_C/(K_H+K_C), net power is P = K_eff(1−x)(T_H−T_C/x), valid for T_C/T_H < x < 1. Efficiency is 1−x. These equations define a particular steady or cycle-averaged model, not every finite-time engine.
Differentiation gives dP/dx = K_eff(−T_H + T_C/x²). Its interior maximum is x = √(T_C/T_H). Here θ_H ≈ 512.132 K, θ_C ≈ 362.132 K, maximum power ≈ 257.359 W and efficiency there ≈ 0.292893. The same model approaches the Carnot efficiency 0.500 as the heat-transfer driving differences and power approach zero.
The expression 1−√(T_C/T_H) is therefore an efficiency at maximum power for these stated conductance and internal-reversibility assumptions. It is not a new universal upper bound on all real engine efficiencies. Different losses, transfer laws, constraints or optimization objectives can give different results. This example explains why “best efficiency” and “largest useful rate” are different design questions.
This model’s maximum power occurs before its efficiency limit
A single honest power-versus-efficiency curve shows the bounded endoreversible linear-conductance model, its interior maximum and its two zero-power limits. The maximum-power efficiency is expressly model-dependent.
Keep axis labels and maximum-point annotation readable; the complete table scrolls locally.
- Blue solid curve and circles: assigned finite-conductance model.
- Orange diamond: model maximum-power point.
Maximum power ≈ 257.359313 W at η ≈ 0.292893.
At that point: θ_H ≈ 512.132034 K and θ_C ≈ 362.132034 K.
External reservoirs: T_H = 600 K and T_C = 300 K.
K_H = K_C = 10.0 W/K; K_eff = 5.00 W/K.
Hollow endpoint at η = 0.500, P → 0: reversible-efficiency limit for finite conductance.
Hollow endpoint at η → 0, P → 0: no useful work fraction.
Curve endpoints are mathematical limits of the open operating domain T_C/T_H < x < 1.
The internal engine is reversible; finite-temperature external heat transfer is irreversible.
η at maximum power = 1 − √(T_C/T_H) for this model, not a universal engine bound.
P = K_eff(1 − x)(T_H − T_C/x).
Linear axes: η = 0–0.500 and P = 0–280 W.
Largest power and largest efficiency are different objectives under these assumptions.
Internal temperatures and hot/cold energy rates identify the curve and its limiting cases.
| Point | η | θ_H (K) | θ_C (K) | Hot input (W) | Cold rejection (W) | Net power (W) |
|---|---|---|---|---|---|---|
| reversible-efficiency limit | 0.500000 | 600.000000 | 300.000000 | 0.000000 | 0.000000 | 0.000000 |
| x = 0.51 | 0.490000 | 594.117647 | 303.000000 | 58.823529 | 30.000000 | 28.823529 |
| x = 0.60 | 0.400000 | 550.000000 | 330.000000 | 500.000000 | 300.000000 | 200.000000 |
| x = 0.70 | 0.300000 | 514.285714 | 360.000000 | 857.142857 | 600.000000 | 257.142857 |
| x = 0.80 | 0.200000 | 487.500000 | 390.000000 | 1125.000000 | 900.000000 | 225.000000 |
| x = 0.90 | 0.100000 | 466.666667 | 420.000000 | 1333.333333 | 1200.000000 | 133.333333 |
| x = 0.99 | 0.010000 | 451.515152 | 447.000000 | 1484.848485 | 1470.000000 | 14.848485 |
| maximum power | 0.292893 | 512.132034 | 362.132034 | 878.679656 | 621.320344 | 257.359313 |
| zero-efficiency limit | 0.000000 | 450.000000 | 450.000000 | 1500.000000 | 1500.000000 | 0.000000 |
Further: a compact second-law audit of a cycle
Entropy S is a state quantity used to track a second-law balance. A cyclic working substance has ΔS = 0. For the device plus two constant-temperature reservoirs and no additional uncounted effects, reservoir entropy changes give total entropy generation S_gen = Q_C/T_C − Q_H/T_H for an engine, or S_gen = Q_H/T_H − Q_C/T_C for a refrigerator. It must be nonnegative, with zero in the globally reversible limit.
For the assigned engine, S_gen = 1200/300 − 2000/600 ≈ 0.666667 J/K per cycle. The rejected candidate with Q_C = 800 J instead gives about −0.666667 J/K. The negative value shows that its energy-conserving ledger is incompatible with the stated second-law boundary.
For the opening refrigerator, S_gen = 1600/300 − 1200/270 ≈ 0.888889 J/K per cycle. Setting the generation to zero recovers the reversible heat ratio and the COP bounds. A nonnegative value is a necessary audit; it does not by itself prove that suitable materials, pressures, phase states, controls or heat-exchanger rates can realize a proposed machine.
Finite sources, extra reservoirs, material flows, heat leaks and changing stored energy require their corresponding entropy and energy terms. Do not substitute a working-fluid temperature for the reservoir temperature without identifying the thermal boundary. “Entropy and the second law” develops this framework; this return section applies only the bounded cyclic audit needed to evaluate the performance claims here.
Check a performance claim from its physical boundary
First identify the useful output: net work, cooling heat removed or heating heat delivered. Draw the system boundary and all heat, work and mass exchanges. Specify whether the claim concerns one complete cycle, steady operation, startup or a season, and whether temperatures describe reservoirs, refrigerant states or a changing finite load.
Close the energy balance with consistent signs, units and counting basis. Form η or the appropriate COP using that same boundary, then compare only with a limit whose assumptions match it. Check kelvin temperatures, auxiliary loads, heat-source changes and whether the stated power or capacity is also physically supported.
A useful model can be simple: the opening refrigerator has one cold-side input, one work input and one larger warm-side output. More detailed component and gas-cycle models explain where those exchanges occur and why losses matter. Their strength comes from retaining conditions, rather than treating a convenient efficiency formula as the machine itself.
Worked examples
Follow both energy inputs
A cyclic refrigerator removes 1200 J and receives 400 J of work. Find warm-side delivery and both COPs.
- Use zero net stored-energy change: Q_H = Q_C + W_in = 1600 J.
- Cooling COP is 1200/400 = 3.00; heating COP is 1600/400 = 4.00.
- The same device and boundary give COP_HP = COP_R + 1.
1600 J reaches the warm side. COP above one reflects heat moved from the cold source as well as work input.
Per-cycle energy and average power
The assigned engine receives 2000 J and rejects 1200 J per cycle at 5.00 cycles/s.
- Net work is 800 J per cycle, so η = 800/2000 = 0.400.
- Multiply each transfer by 5.00/s: input 10.0 kW, rejection 6.00 kW, work 4.00 kW.
- For 600/300 K reservoirs, the reversible efficiency is 0.500; the assigned 0.400 is below it.
The model delivers 4.00 kW net at 40.0% thermal efficiency, not 10.0 kW of work.
An energy ledger can still be impossible
Could the same two-reservoir engine receive 2000 J, reject 800 J and deliver 1200 J?
- The first law closes: 2000 = 800 + 1200 J.
- But η = 0.600 exceeds 1−300/600 = 0.500.
- Its two-reservoir entropy generation would be 800/300−2000/600 ≈ −0.666667 J/K.
No, under the stated complete-cycle, two-reservoir conditions. Additional effects would change the claimed system.
Use an absolute-temperature bound
For the opening 270/300 K reservoirs, find minimum work to remove 1200 J.
- Reversible cooling COP is 270/(300−270) = 9.00.
- Minimum work is 1200/9 ≈ 133.333 J.
- The assigned actual input of 400 J is larger; the bound does not predict the actual device.
At least 133.333 J in the reversible limit, using kelvin ratios.
Include the stated auxiliary input
Deliver 6000 W with compressor heating COP 3.20 plus 200 W dissipated outside the heated envelope.
- Compressor power is 6000/3.20 = 1875 W; source heat is 4125 W.
- Whole-system wall input is 1875+200 = 2075 W.
- Useful whole-system COP is 6000/2075 ≈ 2.891566; one-hour wall energy is 2.075 kWh.
The compressor COP and whole-system COP describe different declared input boundaries.
Convert a component ledger into rates
Use synthetic h₁=400, h₂=450, h₃=h₄=250 kJ/kg and mass flow 0.0200 kg/s.
- Compressor input is 50 kJ/kg, condenser output 200 kJ/kg and evaporator input 150 kJ/kg.
- Multiply by 0.0200 kg/s and 1000: 1000, 4000 and 3000 W.
- COP_R = 3000/1000 = 3.00 and COP_HP = 4000/1000 = 4.00; 4000 = 3000+1000 W.
The energy budget closes, but these h values alone do not establish real refrigerant phase states or pressures.
Close the reversible gas cycle
Use the assigned one-mole Carnot gas cycle with hot isothermal volume ratio 2 and 600/300 K reservoirs.
- Hot isothermal heat is nRT_H ln2 ≈ 3457.888 J.
- Cold rejection magnitude is nRT_C ln2 ≈ 1728.944 J.
- The adiabatic work transfers cancel in this model, leaving net work ≈ 1728.944 J.
Efficiency is 0.500. Signed branch heat and work, not an arbitrary loop drawing, establish the result.
State the model behind a compression-ratio formula
Find ideal Otto efficiency for r=8.00 and constant γ=1.40.
- The reversible adiabats give T₂/T₁ = T₃/T₄ = r^(γ−1).
- Inserting those relations into Q_C/Q_H gives η = 1−r^(1−γ).
- For the assigned model η ≈ 0.564725; heat addition/rejection occur at changing temperature.
About 56.4725% for this closed constant-γ surrogate, not a real engine rating or a comparison at the Carnot example’s reservoir temperatures.
Optimize the stated finite-conductance model
Where does P=K_eff(1−x)(T_H−T_C/x) peak for the assigned 600/300 K model?
- Differentiate: dP/dx = K_eff(−T_H+T_C/x²).
- Its interior zero is x=√(T_C/T_H)≈0.707107; the second derivative is negative.
- With K_eff=5.00 W/K, power is about 257.359 W and efficiency 1−x≈0.292893.
Maximum power occurs below the model’s reversible-efficiency limit. The result is conditional on this heat-transfer model.
Try it yourself
Does ΔU=0 over a cycle mean there was no heat or work?
Show the answer and reasoning
No.
It means the final state energy equals the initial state energy. Nonzero heat and work transfers can balance.
For an engine, are both positive magnitudes Q_H and Q_C heat into the working substance?
Show the answer and reasoning
No.
Q_H enters, while Q_C leaves. The signed cycle heat is Q_H−Q_C.
Does COP_HP=4 violate energy conservation?
Show the answer and reasoning
No.
Delivered heating includes cold-source energy and work input. COP is not a heat-to-work efficiency.
Can one always add one to a catalog cooling COP to predict a separate heating test COP?
Show the answer and reasoning
No.
COP_HP=COP_R+1 requires the same cycle, operating point and boundaries. Different tests and auxiliaries change the comparison.
Can an open electric refrigerator cool the whole otherwise closed room containing it?
Show the answer and reasoning
No under the stated boundary.
Its internal heat redistribution cancels in the room balance; its work input adds room energy.
May 0 °C and 30 °C be inserted directly into the Carnot COP ratio?
Show the answer and reasoning
No.
Absolute-temperature ratios require kelvin. Celsius offsets cancel in differences but not ratios.
The assigned refrigerant loop removes 3000 W from the cold region while receiving 1000 W of shaft work. Find its cooling COP and warm-side heat rate. Which value describes its cooling capacity?
Show the answer and reasoning
COP_R = 3.00, warm-side delivery = 4000 W, and cooling capacity = 3000 W.
Use the same steady loop boundary: COP_R = 3000/1000 = 3.00 and Q̇_H = Q̇_C + Ẇ_in = 3000 + 1000 = 4000 W. The dimensionless COP is a ratio; the 3000 W cooling capacity is a heat-removal rate.
Does reversing a compressor motor make a valve-based refrigerator reversible?
Show the answer and reasoning
No.
The actual loop has component roles and irreversibilities. A reversible reverse cycle requires all changes and external effects to reverse without residual change.
Does an approximately adiabatic throttle with h₃=h₄ deliver turbine shaft work?
Show the answer and reasoning
No under the stated conditions.
The valve has no shaft-work term and is generally irreversible. Equal enthalpy does not mean equal entropy or universal cooling.
Do the four supplied synthetic h values prove a dry vapor compressor inlet?
Show the answer and reasoning
No.
Pressure, temperature, composition and phase/property information are also required. The ledger establishes only its stated energy accounting.
Does diverging reversible COP as lift tends to zero imply unlimited cooling capacity?
Show the answer and reasoning
No.
That ideal ratio does not guarantee a finite driving temperature difference, heat-transfer rate or machine capacity.
Would the building example’s useful COP stay exactly 6000/2075 if the 200 W auxiliary heat instead entered the room and counted as useful delivery?
Show the answer and reasoning
No.
The useful-output boundary would change; its 6000 W stipulated condenser output must be distinguished from additional indoor dissipation.
Does the assigned Otto efficiency exceed the assigned Carnot example at the same reservoir conditions?
Show the answer and reasoning
That comparison is not at the same conditions.
The Otto surrogate has a different temperature range and variable-temperature heat exchange. The examples retain separate assumptions.
Is 1−√(T_C/T_H) a universal efficiency limit for all engines?
Show the answer and reasoning
No.
It is the efficiency at maximum power for the stated endoreversible linear-conductance model; other constraints and loss laws can differ.
Does S_gen≥0 alone prove a proposed refrigerator can be built with the specified phase states and capacity?
Show the answer and reasoning
No.
It is a necessary second-law check. Property, material, component, rate and control feasibility still require evidence.
Is a seasonal COP generally an unweighted arithmetic mean of point COPs?
Show the answer and reasoning
No.
It is formed from total useful energy and total relevant input energy under the declared conditions; operating durations and loads matter.
What to carry forward
- A cyclic working substance returns to its state while heat, work and reservoir changes remain.
- An engine delivers Q_H−Q_C as net work; a refrigerator/heat pump receives that work difference to move heat uphill.
- COP_R and COP_HP count different useful outputs; their difference is one only for the same cycle and boundary.
- Carnot limits use absolute reservoir temperatures and globally reversible operation; they are not measured performance or finite-capacity predictions.
- Vapor-compression and ideal gas cycles explain distinct mechanisms, with stated enthalpy, phase, pressure–volume and caloric assumptions.
- Auxiliaries, temperature lift, losses, heat-transfer rates and complete energy/second-law boundaries decide what a performance figure means.
References
Sources for the concepts and teaching approaches in this article.
- Thermodynamics and Chemistry, second edition, version 10 (2020)Howard DeVoeTextbook chapter · PDFThermodynamics and Chemistry, second edition, version 10 (2020)Sections 4.2–4.3: cyclic engines, Carnot reversibility and temperature limitsSections 4.5–4.6: entropy balance and irreversible changes
- Thermodynamics and Propulsion: Unified Engineering lecture notesE. M. Greitzer, Z. S. Spakovszky and I. A. WaitzCourse notesThermodynamics and Propulsion: Unified Engineering lecture notesSection 3.3: the Carnot cycleSection 3.4: refrigerators and heat pumpsSection 3.5: ideal Otto cycle and its assumptionsSection 3.7: Brayton cycles and net workSection 8.5: Rankine power cyclesSection 8.6: enhancements and operating parameters of Rankine cycles
- Basic Thermodynamics: lecture 31, Refrigeration CycleY. V. C. Rao and Gautam BiswasCourse notesBasic Thermodynamics: lecture 31, Refrigeration CycleVapour-compression cycle and component enthalpy balancesAbsorption refrigeration and its thermal input
- Efficiency of a Carnot Engine at Maximum Power Output, American Journal of Physics 43, 22–24 (1975)F. L. Curzon and B. AhlbornResearch paperEfficiency of a Carnot Engine at Maximum Power Output, American Journal of Physics 43, 22–24 (1975)Original paper PDF, institutional mirror
- Air Source Heat Pumps in Cold Climates: presentationTom Marsik and Vanessa StevensTeaching resource · PDFAir Source Heat Pumps in Cold Climates: presentationSlides 3–5: heat sources and heating COPSlides 9 and 13–17: operating conditions, cycling and field-performance limits